"Chris Cole" <chris.cole@finisar.com> writes:

One of the points made by Ted Sealy from Sprint is that they take
advantage of the extra link budget in 10GBASE-LR 10km link budget to
account for extra connector loss, etc.

Ted Seely and I are of the same mind on this. 2 dB sounds like plenty
for connector loss right up until you have to deal with multiple patch
bays in a structured system with amateurishly applied mechanical
splices. The difference between noting that the loss is a little high
but the link still works so you roll with it, and having to spend time
on the phone arguing with someone who thinks 24 dB link loss is A-OK,
will make the slight additional up front cost for the better grade
optics look very inexpensive indeed...

From this discussion it sounds to me like we should stick with 10km
initially, and then later come back with an additional specification
optimized for low cost, perhaps covering 2km.

I'm on board with that as far as it goes, but has the scenario of
adjustable launch powers so that you don't ever need attenuators plus
the economy of scale that would come from having *one* type of
interface for 1m-10km runs been considered? It seems to me based on
what I've seen of the optics market that once you make something a
mass-produced commodity the price falls awfully far - suppose the
price difference was $250 vs. $375, that's a big difference on a
percentage basis but pocket change on an absolute basis.

                                        ---rob

I'm on board with that as far as it goes, but has the scenario of
adjustable launch powers so that you don't ever need attenuators plus
the economy of scale that would come from having *one* type of
interface for 1m-10km runs been considered? It seems to me based on
what I've seen of the optics market that once you make something a
mass-produced commodity the price falls awfully far - suppose the
price difference was $250 vs. $375, that's a big difference on a
percentage basis but pocket change on an absolute basis.

I'm inclined to agree that when we are talking about unit numbers between 10km >> 40km optics, the marginal price change of a few bucks per optic (vs the human time to go and fix/groom/find/reduce optical losses) is pretty minimal.

For that 1% of customers that finds their total cost significantly impacted (vs, say the cost of the equipment these are going into, etc).... would force 10% of us to have to engineer bypass cross-connect panels with fewer physical connections (and spliced ones at that) to get the job done.

Just my guess... but no one has really complained about 10km reach optics being so expensive after the first 5 minutes they've been on the market.

Personally, I wish this much cost could be cut out of the 80/120km optics market... but hey, no one is asking me.

Deepak

Deepak Jain <deepak@ai.net> writes:

I'm on board with that as far as it goes, but has the scenario of
adjustable launch powers so that you don't ever need attenuators plus
the economy of scale that would come from having *one* type of
interface for 1m-10km runs been considered? It seems to me based on
what I've seen of the optics market that once you make something a
mass-produced commodity the price falls awfully far - suppose the
price difference was $250 vs. $375, that's a big difference on a
percentage basis but pocket change on an absolute basis.

I'm inclined to agree that when we are talking about unit numbers
between 10km >> 40km optics, the marginal price change of a few bucks
per optic (vs the human time to go and fix/groom/find/reduce optical
losses) is pretty minimal.

For that 1% of customers that finds their total cost significantly
impacted (vs, say the cost of the equipment these are going into,
etc).... would force 10% of us to have to engineer bypass
cross-connect panels with fewer physical connections (and spliced ones
at that) to get the job done.

Just my guess... but no one has really complained about 10km reach
optics being so expensive after the first 5 minutes they've been on
the market.

Personally, I wish this much cost could be cut out of the 80/120km
optics market... but hey, no one is asking me.

So, the unspoken point of what I was suggesting is "why not two kinds
of optics: medium to short and super-long?? Simplifies sparing.

                                        ---Rob

This is somewhat interesting subject. The optical margins for "short-haul"
optics are getting tighter. The number of crossconnects in a structural
wiring system is getting larger. Given the specified SC connector
insertion loss of .75dB, it is not uncommon to see loss within a facility
for "working" crossconnects of 3-4dB.

Is anyone giving thought to going forward to connectors like MU/E2000 for
structured wiring (which have much lower specified loss - I believe .1dB),
or the installed base makes it prohibitive?

-alex [not mlc anything]

Where does this .75 dB figure come from? Googling around seems to yield .15-.5 with a typical around .2. .75 sounds very high.