DataCenter color-coding cabling schema

Hello Nanog-ers,

Have any of you had the option or; conversely, do you know of “best
practices" or “common standards”, to color code physical cabling for your
connections in DataCenters for Base-T and FX connections? If so, Could you
share any ttype of color-coding schema you are aware of ?…. Yes, this is
actually considering paying for customized color-coded cabling in a Data
Center...

Mr. Google did not really provide me with relevant answers on the above…
beyond the typical (Orange is for MMF, yellow for SMF, etc)…

Any reasons for or against it welcome too...

I know at Clearwire data centers we used gray for network, blue for
management and orange for RS-232 console. At least for the initial build.
Later re-work or additions were whatever the tech had on hand :wink: They also
had labels on each end of each wire showing the path through the system,
sometimes up to six lines. It did make it easy to bring up a data center
and find cabling errors. To see the system last more than a year or two up
upgrades would take some strong rules and oversight. I think it would be
worth it if your management system can keep the religion.

I don’t know of any universal standards, but I’ve used the following in several
installatins I was responsible for to good avail:

Twisted Pair:

RED: Untrusted Network (Internet or possibly DMZ)
YELLOW: Optional for DMZ networks though I preferred to avoid documented in [1] below
BLUE: Trusted Network (back-end, internal, etc.)
GREEN: RS-232 straight-thru
PURPLE: RS-232 X-Over (effectively Null Modem) 12345678 <-> 87654321 pin map.
ORANGE: Ethernet X-Over (Best avoided documented in [2] below)
GREY: Special purpose cabling not in one of the above categories

Fiber:
Orange — Multimode Fiber
Yellow — Singlemode Fiber

The absolute most useful thing you can do if you can impose the discipline to update
the cable map rigorously and/or allocate manpower for periodic audits is to apply a
unique serial number to each cable. I preferred to document not only the cable ID,
but also the length. For the installations where I have worked, 5 digits was sufficient
unique ID, so I used formats like IIIII-L[.L] where IIIII was a unique ID and L.L was
the length of the cable in feet. (e.g. 00123-6.5 is cable number 123 which is 6.5 feet
in length).

The labels are (ideally) the self-laminating wrap-around types. I prefer the Brady
labeling system which will automatically print 2-4 (depending on font size) instances
of the label text on the self-laminating label such that it can be read from virtually
any side of the cable without requiring you to rotate the label into view in most cases.

The Brady labeling system is a bit overpriced compared to the Brother P-Touch, but the
expanded capabilities and the quality of the label adhesives and such is, IMHO, sufficiently
superior to justify the cost.

Whatever you do, please do not use Flag labels on cables… I HATE THEM. They are a constant
source of entanglement and snags. They often get knocked off as a result or mangled beyond
recognition, rendering them useless.

Similarly, I’ve found that circuit-ID and end-point labels on cables are often ill-maintained,
so if you do use them, please make sure you remove them when the cable is moved/removed.

The length is very useful because it gives you a radius within which the other end of
the cable must be located and you can usually expect it to be reasonably close to the
outer edge of that radius.

More than a few times I’ve prevented a serious outage by giving the port number to the remote
hands guy and then insisting that he read me the cable ID. “No, try the other port
FE-0/2/4… You’re off by one. It’s above/left/right/below you.”

[1] I prefer to avoid Yellow cables because some people have trouble understanding
that Yellow Fiber and Yellow UTP might have different meanings. I also feel that the
distinction between UNTRUSTED and DMZ networks is usually not all that important in
most cabling situations. YMMV.

[2] In this era of Auto-MDI/MDI-X ports and the like, it’s very rare to encounter a
situation that truly requires a crossover cable with no viable alternative. If such
is needed, I prefer to document it on the cable tags rather than using a special color
code. Again, you have the risk of people not understanding that orange Fiber might not
mean what Orange copper means. YMMV

Yes, I know you can now get virtually any type of fiber in virtually any color, but
the simple fact of the matter remains that when you send skippy out to buy emergency
jumpers or such, you’re most likely going to either get orange multimode or yellow
singlemode and that’s just the way it is.

Owen

Hi Yardiel,

Patch cables or fixed cabling to patch panels?

For fixed cabling, it's common to pick colors which match the cable
type. Orange for multimode fiber, yellow for single mode fiber, blue
for four-pair cat5e, something else for cat6, etc. At each end, label
the location of the opposite endpoint twice, once on the panel and
once on the cable itself (cables can pull loose from panels).

With fixed cabling terminating in patch panels they'll tend to get
reused over time for different types of signalling so don't overthink
it.

For patch cables, it's common to pick a color for each type of
physical signaling so you don't jam the wrong kind of signal in to a
port that doesn't match. Your gig-e switch may not like the voltage
from that ringing pots line. Blue for ethernet, white for POTs, green
for T1s, some other color for the rs232 serial cables, IP/KVM cables,
etc.

I find the easiest way to label patch cables is with color electrical
tape. Put the same bands of unique colors at both ends of the cable.
This will let you visually identify the cables without pulling on them
to try and line up tiny text on the tags with your eyeballs.

Regards,
Bill Herrin

Hi,

What is the best solution for thin 2 mm or 0.9 mm fiber labelling? I like
the idea of wrap around labels but does that work on thin wires? Maybe use
something to pad the wire to more thickness where the label is to be?

Regards,

Baldur

Hi Baldur,

Equinix in Sydney use the below, for Cross Connects.

Goes around the fiber to pad it out, and the label keeps it on the fiber.

http://www.cableorganizer.com/panduit/labelcore-cable-id-sleeve/

Been meaning to order some for internal use, too.

Nick

I doubt it would work on 0.9mm single strands, but I’ve had reasonably good
luck with it on standard SM and MM fiber pairs with normal zip-cord style
sheathing.

Owen

The only problem I’ve had with those is that they tend to slide down the fiber and you can
end up having to trace the fiber to find the label which sort of defeats the purpose.

Owen

Just place a piece of tape under the padding and it won't slide anymore. 5
seconds of extra work per end, though.

I dunno. Your dexterity must be better than mine. I'd have trouble digging up
the roll of tape, removing a section, putting the tape roll down, and applying
the tape to the cable, all in 5 seconds.

Especially if you drop it and it manages to bounce through a cutout in the
raised floor. That's got to be the single best reason for overhead cabling. :slight_smile:

I used to support this view too, but over the last few years, as everything
has (basically) become Ethernet, I've taken to a different scheme.

For copper patching, I now recommend my clients simply invest in a range of
colored patch cables and use them randomly.

The length of the patch cable is much more important than the color (too
little length will make it difficult to re-route cables if you need to
remove cards etc. and too long will mean tangles and space taken up with
loops of excess cable.)

The benefits of my "rainbow" scheme are:

1. easier to identify both ends of a cable, reducing disconnect errors.
When tracing a cable in a bundle or on a patch bay, it's easy when they're
different colors.

2. no need to police the cable scheme - if you have a strict color regime,
what do you do when someone uses the wrong color? especially if a
disconnect would be service affecting. It's really hard to justify
"maintenance downtime" to an account manager on the basis of you not liking
the color of a patch cable.

Aled

Hi,

I'm not sure I'm keen on a colour standard - especially given our recent difficulties
sourcing cabling to our spec in certain colours...or lengths! however, what we do - and others
do based on this thread - is have our own internal colour scheme for purposes/systems/customers.

fibre is far more difficult for this - coloured labels (and a decent labelling regime in the first place)
win in that arena. (obviously the copper plant has labelling too but the choice of colours means
that function/purpose is already known from many metres away :wink: )

alan

Sun, Mar 13, 2016 at 05:10:26PM -0700, Owen DeLong wrote:

Whatever you do, please do not use Flag labels on cables… I HATE
THEM. They are a constant source of entanglement and snags. They
often get knocked off as a result or mangled beyond recognition,
rendering them useless.

Hadn't seen that for ages, using Brother P-touch printers for
small amounts of work and Avery Zweckform paper + laser printing
for large cable installations. This stuff (Avery paper),
  http://computing.kiae.ru/~rea/wiring-porn-2.jpeg
lives already for 5+ years and outlived many replacements of
spine modules (that's InfiniBand fabric) and other operations
without labels being ruined in any way.

Lol! I am very dextrous... But I prep by pulling off many pieces of tape at
once and lining them up in advance. They don't need to go on perfectly. In
fact, a few wrinkles help to keep the padding in place better than no
wrinkles.

Put a wire around the roll of tape and connect it to a small carabiner that
you can clip to the rack or to other stable items wherever you're working
(not individual cables in case you dislodge them).

Because it’s faster if you have to climb down off a ladder first before pulling
up the floor tiles to track down the roll of tape?

Oh, you mean that’s the single best reason for overhead COOLING. :stuck_out_tongue:

Owen

Have any of you had the option or; conversely, do you know of “best
practices" or “common standards”, to color code physical cabling for

your

connections in DataCenters for Base-T and FX connections?

For patch cables, it's common to pick a color for each type of
physical signaling

I used to support this view too, but over the last few years, as everything
has (basically) become Ethernet, I've taken to a different scheme.

For copper patching, I now recommend my clients simply invest in a range of
colored patch cables and use them randomly.

The length of the patch cable is much more important than the color (too
little length will make it difficult to re-route cables if you need to
remove cards etc. and too long will mean tangles and space taken up with
loops of excess cable.)

The benefits of my "rainbow" scheme are:

1. easier to identify both ends of a cable, reducing disconnect errors.
When tracing a cable in a bundle or on a patch bay, it's easy when they're
different colors.

But if you serialize them and have the company you order the cables from
do the labeling (I’ve had this done, it’s not difficult and doesn’t add
significantly to the cost of the cables), then that’s even more useful
for that purpose than your “rainbow” scheme.

2. no need to police the cable scheme - if you have a strict color regime,
what do you do when someone uses the wrong color? especially if a
disconnect would be service affecting. It's really hard to justify
"maintenance downtime" to an account manager on the basis of you not liking
the color of a patch cable.

Well…

1. You have someone whose responsibility it is to keep appropriate
  sized cables of various colors in stock so that there’s no incentive
  to do so.

2. You don’t let untrained monkeys play in your cage.

3. You hand the 1d10t that did it a roll of appropriately colored electrical
  tape and provide instructions on how to spiral-wrap. He gets to change the
  color of the cable. (This will make a repeat offense relatively unlikely
  as it’s a huge PITA).

Owen

Sorry… To be clear, those hideous attrocities of P-Touch nastiness
are exactly what I meant by flag labels. I had forgotten about the
plastic zip ties with the over-sized surface on the ratchet.

Compare to:

http://www.cableorganizer.com/images/brady/brady-idxpert/labels-markers/images/01-idxpert-markers-labels-cables.jpg

http://neumannmarking.com/wp-content/uploads/2015/03/135866255-300x199.jpg

http://www.hotblog.co.uk/boblittlepr/wp-content/uploads/2013/06/cable-labels_Cormant_1.jpg

Admittedly, I’m not wild about the bar-code scheme in the last one as I prefer human-readable labels, but YMMV.

Owen

The tiles intended for cold air flow have lots of little 1/4" or so holes
in them that a roll of tape can't fall through. The roll of tape *can*
escape through the 6x6 cable cutout under the rack if there aren't too
many cables in the way. If we had overhead cabling and under-floor cooling,
we'd have no large cutouts anyplace. :slight_smile:

(Alas, the data center across the hall is 27 years old, and we'll need to
build a new one to fix it. Someday soon, maybe. :slight_smile:

That's the issue, keeping it that way. "Gray for network" is likely to result in mostly gray cables which won't really help to differentiate things in the long run. Breaking it down further can get tricky in terms of definition. Each network has a color, but then there's this trunk link....

We had a customer who had a scheme involving five different colors. When they did the initial build their wiring vendor came in with barrels of new cables of various lengths and colors and it looked really nice with cable management and all.

After a couple of years it was pretty much random in terms of color coding. Keeping multiple lengths on hand for dressing in raceway without incurring either tons of slack or bow-string taut wires is tough but possible, doing that in half a dozen colors can be daunting.

The electrons on the inside can't see the jacket on the outside and most of them are rumored to be color-blind anyway.

Maybe a compromise of a single color for most things and a different one for specials.

Yes and no.

If you have a requirement that all cabling between racks goes via fixed cabling from patch panels and patch cables are only used for intra-rack runs between equipment in the same rack and/or equipment<->patch panel in the same rack, it gets a lot less so. This can also help keep a lot of other things more sane in the long run as well.

I found that you could deal pretty well with any intra-rack run (assuming 7’ racks) if you stocked the following lengths:

  0.5’
  1’
  1.5’
  2’
  2.5’
  3’
  4’
  5’
  6’
  7’
  8’
  10’

That’s a total of 12 lengths. We kept those in stock in Yellow (SMF), Orange (MMF), Other colors all Cat 6: Blue, Red, Purple, Green.

Total of 72 part numbers to keep track of. We got one of those roll-around bin carts that had 4 rows of 9 drawers on each side. Worked out perfectly to have 72 kinds of cables. (IIRC, we did 3 columns per color working up in size from left to right).

We had a guy who was responsible for making sure none of the bins were ever empty. I think he checked the cart twice a week and ordered once a month most months. I think we tended to keep at least 5 on the cart and topped the bins up to 20 for most sizes and 40 for the popular size/color combinations.

We didn’t have any trouble maintaining the system and as long as the right color was available, we got pretty good compliance from the people installing cables. (Our “retraining” method for people who ran a wrong-colored cable didn’t hurt, either.)

YMMV.