Data Center AC Issues

Are you monitoring your line voltage?
I've seen "normal" AC lines, in the US, anywhere from 70-140VAC.
Modern equipment use switcher power supplies, which draw more current as the voltage goes lower.
Heat in the power supply is a function of current squared.
So, as the line voltage goes lower, the equipment gets hotter.
(paradoxical-seeming, ain't it?)