RE: DC power versus AC power

For those AC only powered units, you can also purchase an invertor
for DC to AC conversion. You would then have the advantages of DC
for your AC equipment. This does, however, add the potential of
another point of failure such as fuses or breakers in the invertor.

Not to mention additional cost of wasted electricity (which does add up
significantly when it is anything but a spot solution) and pitfalls of
inverters (like their imperfect sine waves). And if you're putting spot
solution UPS units out into the bottom of a particular rack, be ware their
canny ability to catch fire when the price is right.

Inverters or rectifiers should be point solutions in a plant layout. If you
have a lot of AC & DC, get two protected plants. Only way to live.
Sometimes that's not just nice to have, but simply required.

If you're primarily a systems shop and have environmentally conditioned
space, get AC. If you're in a nasty colo spot, with poor environmental
(read: not guaranteed meat locker climate 24x7), get DC & NEBS hardware or
hardware which meets NEBS almost entirely but doesn't carry the sticker for
some silly reason such as "easily flammable plastic used for front grill".
Depending on what your colo requires. There are many different flavors of
colo.

Speaking of flavors, consider the impact of a turf vendor based on whatever
decision you chose when going into colo space. May or may not be an issue.

See what equipment offers what, do the math on cost of plant and gear, pros
& cons. And make a business decision based on engineering data. (uh, right)

But, as Stephen already eluded to... Compared with an AC plant design, to
me, one of the biggest drawbacks of a DC plant is safety (I have had to
kick a fellow worker away from the rack before). One of the biggest
advantages is simplicity of design when it comes to battery plant.

There is no universal answer, it all depends. And one ends up shuffling off
and having to do a bunch of homework.

Of course, this is all IMHO and I've been wrong before.

Thanks,
Christian

Not to mention additional cost of wasted electricity (which does add up
significantly when it is anything but a spot solution) and pitfalls of
inverters (like their imperfect sine waves). And if you're putting spot
solution UPS units out into the bottom of a particular rack, be ware their
canny ability to catch fire when the price is right.

Switched power supplies really don't care about the quality of the sine
waves that feeds them, as long as they have energy to put into the "tank".
On the other hand, video monitors like sine waves, and they may not get
along with DC inverters/rectifiers (or even portable AC no-breaks, which
usually generates AC from DC).

Rubens Kuhl Jr.

me, one of the biggest drawbacks of a DC plant is safety (I have had to
kick a fellow worker away from the rack before). <<

What was the worker doing? Is this 48 VDC?

Thanks,

--Michael