100 meters is, in fact, the distance limitation for Fast Ethernet, but you
can usually exceed that if the link is full duplex. Note that I'm not
recommending that you do so, just stating that it is possible.
If your run length is more than 100 meters, and you're running half duplex,
then I would say that is definitely your problem.
putting a shield on cat5 or 6 cable doesn't significantly increase the
noise rejection vs utp cat 5 at 100mb/s, you're shielding already
balanced cable pairs.
moreover they're signifcantly harder to install since they need to be
properly grounded and shielded at both ends.
In the "me too" category, I've seen a company install wireless on top of
the Netherland's highest building (The Rembrandt's tower), which included
using a lightning arrestor, and not ground it.
It only took 3 storms (and 3 wireless cards) before they finally decided
to ground the thing, and at the time, they weren't that cheap either
AGREED, one end and one end only, or youre asking for a ground loop....ground the end with the best, shortest path to earth ground.....in his case, that would prob be the telco room end, "usually" theres a decent ground there somewhere.....
Mileage may differ...
Anybody else ever chased a grounding wire you suspected wasn't doing its job,
only to find that it was quite securely clamped to a large drain pipe only 4
feet from where it left the building? Sounds good, except that the pipe
transitioned from cast iron to PVC 2 feet from the exit point....
How about the di-electric fittings on either a water heater, or a water meter?
Of course, "no one" would use a HOT water line as a ground, but it does happen, and
I believe the NEC requires both be bypassed now with a conductor the same size as power neutral.
I routinely jump unbridged meters and water heaters (cold pipe to hot) with a #6 when in doubt.
Just to be sure.
I've got lots of #6 in the scrap box, and plenty clamps...
AGREED, one end and one end only, or youre asking for a ground
loop....ground the end with the best, shortest path to earth
ground.....in his case, that would prob be the telco room end, "usually"
theres a decent ground there somewhere..... Mileage may differ...
Some hours reading the back issues of the journal found at http://www.compliance-club.com will hopefully inform you why star grounding
is a thing of the past. Ground both ends. If you are afraid of ground
loops, place a heavy (as in 10-16mm2 or AWG way below 10) ground conductor
alongside the signal cable, and ground it firmly in both ends. That will
take the current away from the shields.
Ungrounded shileds are inefficient for EMI and RF shielding, while at times
efficient AC hum blockers.
And, IANAEE, but I've played with big sound systems that exhibit all these
problems.