At GlobalNAPs on the 4th floor at 32 Old Slip, power has been
restored via generator, but all Verizon circuits in the building are
down. Our point to point T1 lines are down and I am guessing that all
IMT trunks into CLECs in the building are also down as a result.
Our GlobalNAPs PRIs are up, but we get a fast busy dialing in.
gnapsny1> sho isdn
D Ports State L1 L2 Change init Up Down
-- ------- ------------- ------- ----- ----- -----
0 S0-S22 UP Active 8:06 2 2 1
1 S24-S46 UP Active 8:06 3 2 2
core1-gnapsny uptime is 8 hours, 4 minutes
System returned to ROM by power-on
System restarted at 07:09:24 UTC Wed Sep 12 2001
At GlobalNAPs on the 4th floor at 32 Old Slip, power has been
restored via generator, but all Verizon circuits in the building are
down. Our point to point T1 lines are down and I am guessing that all
IMT trunks into CLECs in the building are also down as a result.
Yep, our backhauls are on VZ and showing up/down. Kind of odd because
they go to 25 Broadway and only touch the Broad Street CO, which should be
OK. Other T1's out of 25 Broadway are up with the exception of three
customers in the financial district, one in Newark, and one in Queens.
Charles
We have a man back at 32 Old Slip now. Most of our issues came from
overheat. The generators are now up but utility power is still out. There
is emergency lighting only. The generator ran our of fuel once and has been
refilled from the building reserve but we are unsure about getting
addiitonal fuel at this time.
Sincerely,
GLOBAL NAPS, INC.
Vincent J. Bono
Vice President
Engineering
PS
FOCAL is on the 4th floor with us as well as TCG (AT&T Local). AT&T seems
to have an equipment failure.
-vb