In the catagory of stuff happens:
http://www.cnn.com/US/9810/12/la.911.ap/
Does your co-locate have a sump pump?
In the catagory of stuff happens:
http://www.cnn.com/US/9810/12/la.911.ap/
Does your co-locate have a sump pump?
A good reminder. It's not that the National Fire Protection Association
doesn't do a good job, but we need equal time for National XXX Protection
Associations for other threats to facilities.
I was about to say I can easily remember being burned by water even without
Sean's example, although that metaphor is highly suspect. In facilities
for which I've had design or operational responsibilities, I've never had a
fire that caused any problems. Fire protection, on the other hand....
1969...At a Navy site, there was a classified tape vault adjacent to the
main computer room. It had a sprinkler inside, without a sprinkler
alarm. As a true vault with a bank-vault sort of door, there was
very little ventilation. There was no sprinkler alarm. Over a
weekend, the sprinkler inside, which turned out to be defective,
let go. Water rushed into a sealed space, compressing the air
inside.
On Monday, a sailor spun the combination, pulled the door handle...
and was smashed into a wall as the door burst wide. Several broken
ribs, a concussion where the back of his head hit the wall, but no
permanent injuries.
This was a mainframe computer room with a raised floor and
emergency power off, so most water ran under the floor and just
wet cables. Power was interrupted quickly. But it took several
days to dry out and fix components fried by the power-off surge.
The militarized computers weren't particularly bothered, but
the IBM 7090 and UNIVAC 1108 were down for days.
LESSONS LEARNED: Sprinkler alarms in sealed spaces.
Raised floor does give some protection.
1970...building maintenance turned off the heat in the office building over
a long weekend when the building was closed. Temperature dropped to
about 10 degrees F. On Monday, as the heat was back on, sprinkler
pipes that had frozen burst in several walls and ceilings. The most
dramatic spot was the mall beauty shop...people with their heads in
electric hair dryers were NOT amused as water cascaded over them.
Luckily, no electrocutions.
My computer room had a DEC PDP-11 (serial number 1117 -- my remembering
the serial number almost 30 years later should give you a sense how many
service calls I placed on it). No emergency power-off for the room.
In what might have been a medal-winning act of heroism if this were
a military site -- it was the clinical computer room for Georgetown
University Hospital -- one of my colleagues, Scott Dyer, ran into ankle-
deep water to pull electrical plugs before the rising water could get
into the disk cabinet fans, succeeding with seconds to spare.
The only cables actually submerged were RS-232, and where connectors
were underwater, they were tightly screwed together and remained
watertight.
LESSONS LEARNED: Sprinkler systems need heated buildings in cold
climates.
Dry-pipe sprinkler systems, in which no water enters
the piping until a sprinkler head actually releases,
are preferred for equipment rooms.
Emergency power off systems have their uses, although
they can be expensive. Might make sense to tie
underfloor water alarms to emergency power off
1975 or so...more than one occurrence. US Senate off-site computer room, where
we had several computers for the Library of Congress. Senator took a
nap on a hideaway office couch, while smoking. Couch caught on fire and
other office furnishings lit off.
Firefighters put a water stream on it and put it out. Office was on the
4th floor, computer room on 1st floor. Water runs downhill. Water
gushed mostly down stairs; very little came through ceilings at first
but water started dripping (and gushing on one occasion) much later
than the initial flood.
LESSONS LEARNED: After the first occurrence, the Senate people bolted
rolls of plastic sheeting to the ceiling near the
main computers. They stapled a thin wood strip to the
end of the roll plastic, and attached a rope to the
strip. This let an operator grab the rope and quickly
pull protective plastic over the computers. Remember
that if you cover the top, you have probably blocked
cooling and need to power down FAST.
If stairs enter the computer room (e.g., emergency
exit), avoid putting equipment close to them. Water
coming in is an issue -- and a burning computer could
be an exit problem.
Howard